If you short the neutral to the grounding conductor, all you have done is create a parallel path for the neutral current. To find the current that will flow in the grounding conductor, you have to do a parallel circuit calculation based on the current flow in the neutral prior to the short and the impedance's of the neutral and grounding conductors.
Don


Don(resqcapt19)