John,
It means that the pipe coming into the back of the box has been ground flush with the back of the panel and therefore has no locknut or grounding bushing so the conduit cannot serve as the ground(there is not a ground wire pulled in with the circuits.)He is saying that the fitting was not an electrical fitting so it did not meet the requirement of 110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling


[This message has been edited by txsparky (edited 02-06-2003).]


Donnie