Posted By: maintenanceguy Time Domain Reflectometers - 01/31/06 04:51 PM
Can a TDR be used to find faults in electrical installations. I know they'll work on long cable runs but if you tried to use one to find an open wire in a building, would you get a bounce off of every wire nut, lug, and terminal screw between you and the open?
Posted By: NJwirenut Re: Time Domain Reflectometers - 01/31/06 10:34 PM
Yes, you would see every splice and tap, but the reflections from those would be a lot smaller than the reflection from the open conductor.
Posted By: JoeTestingEngr Re: Time Domain Reflectometers - 02/02/06 05:28 AM
I don't think that it would be the technology of choice to hunt down an open in a building though. I would think that some sort of signal injection and sniffing scheme would serve better than a TDR in that application.
Joe