Joined: Dec 2001
Posts: 300
M
Member
Can a TDR be used to find faults in electrical installations. I know they'll work on long cable runs but if you tried to use one to find an open wire in a building, would you get a bounce off of every wire nut, lug, and terminal screw between you and the open?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Sep 2001
Posts: 806
N
Member
Yes, you would see every splice and tap, but the reflections from those would be a lot smaller than the reflection from the open conductor.

Joined: Nov 2005
Posts: 827
Likes: 1
J
Member
I don't think that it would be the technology of choice to hunt down an open in a building though. I would think that some sort of signal injection and sniffing scheme would serve better than a TDR in that application.