Would it be permissible to use sch 80 in a hospital, with two grounds as long as you did not supply patient areas or emergency power through it?(You would still use a mettallic raceway for these areas)
I don't think that you can use PVC in a hospital under any circumstance. I have never seen PVC in the hospital that I worked in.
517.13 a wiring methods,
517.30c(3) Exceptions 3& 4 Essential Electrical Systems
JG, there is no need to put two EGC's in PVC in a hospital.
In the applications where PVC can be used in a hospital, there would be no reqirement for this to be done.
See Yoopersups' code references, as well as 517.12
Roger