Posted By: JSelf Electric Room Labeling? - 10/04/04 09:13 PM
A bit of a dispute here has came up and I was wondering if somebody could clarify. I was almost certain that an electrical closet needed to be labeled "Electrical Closet" or simular on the door for the given closet. In our case it is a bi-fold door with a disconnect, 208v panel, and timeclock/contactor. I have been trying to verify where I thought I read that in the code and I am at a loss..any help would be appreciated.

Thanks,
Jason Self
Posted By: iwire Re: Electric Room Labeling? - 10/04/04 09:17 PM
I do not know of any NEC requirement for this, sometimes the fire dept asks for signage on some or all the electric rooms.
Posted By: e57 Re: Electric Room Labeling? - 10/05/04 12:40 AM
It may be in the UBC or other building codes, but not the NEC. As far as I know. Other entities that may want it marked may be the POCO, if containing a main or meters.
Posted By: Ryan_J Re: Electric Room Labeling? - 10/05/04 01:20 AM
Not a building code requirement, unless a local one. Its not in the IBC, and I don't remember it being in the UBC (97).
Posted By: DougW Re: Electric Room Labeling? - 10/07/04 06:26 AM
I don't think it's in the Code, but I know my town has it as a local (fire) ordinance...