Is it acceptable to run LV conductors in the same conduit with the regular voltage conductors.
For instance, undercabinet lighting with the xfmrs in the basement, run to a kitchen above in EMT with the 120v conductors.

I don't think anything is wrong with it, provided the insulation is rated for the highest voltage on all the conductors.

Any opinions?
Posted By: sparky Re: mixed voltages - 07/16/01 11:35 PM
no Opinion Steve, just confusion, would we need to go to 725-26?
Posted By: Joe Tedesco Re: mixed voltages - 07/16/01 11:51 PM
See Section 300-3(c) Conductors of Different Systems.



[This message has been edited by Joe Tedesco (edited 07-20-2001).]
Posted By: sparky Re: mixed voltages - 07/17/01 12:52 AM
Yes yes,
but i think the original Q was to address Low-V , as in after a 120/12V X-former. Inasmuch as there is no definition of LV.
Posted By: WARREN1 Re: mixed voltages - 07/17/01 12:13 PM
Sounds like he is putting the ballast for a light fixture in the basement. Check the xfmrs secondary output voltage. It may be higher than you think. Of course, if the xfmr is truly a step down version, then as pointed out by Joe Tedesco, all the conductors in the same raceway, enclosure, or cable must be insulated for the highest voltage.
Posted By: sparky Re: mixed voltages - 07/19/01 12:18 AM
http://www.iaei.com/ubb/Forum1/HTML/000376.html

well Steve, this should be interesting!