Posted By: sparky66wv 100 A feeders - 05/16/01 04:53 PM
This has been beat to death in Mike Holt's BB and the DIY BB, but I'm still confused.

My supplier only carries #4/0 and #2 Al SE and SER cables... no other sizes. I realize that the supplier is not infallible...

Bidding around here is hard enough, I can't compete with the ignorant! Just what the heck am I supposed to do with 100A Sub panels? #3 CU THHN in pipe? #3-3 w/G Cu NMB cable (which is unavailable here)? The supplier is clueless, I just called him...

I've been through about $10K of lost bids this week mainly due to sticker shock...

Any venture capitalists out there? I promise not to spend frivolously like the tech companies did...

If not...Anybody wanna buy a slightly used Electrical Business? Just Kidding folks...

[Linked Image]


[This message has been edited by sparky66wv (edited 05-16-2001).]
Posted By: Mike Re: 100 A feeders - 05/16/01 05:12 PM
What wiring methods have you used in the past to install subpanels? You could order what you want to use and keep it in shop stock.
Posted By: sparky66wv Re: 100 A feeders - 05/16/01 05:15 PM
Oh... This is in reference to Table 310-15(b)(6),

100A feed through discos are unavailable here, we generally use load centers for discos (raintite). Does the feeder from the first load center (being used as a disco) to the second (being used as the main panel) qualify as a service feeder, or is it a sub feed??

BTW the EI passed a similar install just a few weeks ago... It was fed from a 200A panel with #2 SER (most around here would have used SE) and was obviously a sub panel.

Would using a main breaker in the sub panel instead of a MLO make any difference in the definition of the intended use of the cable?

This code loop could triple the price of a sub panel install for me and put me out of the competition, I can't be the only one complying with codes that "no one has heard of" around here... and expect to make money, or even get the jobs in the first place!
Posted By: sparky66wv Re: 100 A feeders - 05/16/01 05:22 PM
There appears to be some controversy on whether or not #2 SER is allowed in a sub feed... Sorry I didn't make that part clear...
http://www.mikeholt.com/forum/Forum1/HTML/000545.html
http://forum.doityourself.com/showthread.php?threadid=58652



[This message has been edited by sparky66wv (edited 05-16-2001).]
Posted By: sparky Re: 100 A feeders - 05/16/01 08:51 PM
oh boy,
here we go...someone call for more tankers...
[Linked Image]
personally, i'm confused as to which code overrides which, and what changes have taken place ( or are going to..)

some articles to consider;
T310-15(b)(6) and whatever the 99' change was
338-4(a) brings you to;
336 A&B ends up in
336-26 , note the 60 deg deal...
110-14(c) honorable mention.....
T-310-16 why not....

[Linked Image]
Posted By: sparky66wv Re: 100 A feeders - 05/16/01 09:34 PM
Whoa... looks like that leaves us with a #1/0 Al Sub Feeder for 100A...

Steve or Bill... you got the ROP's on this?

[Linked Image] [Linked Image]

[This message has been edited by sparky66wv (edited 05-16-2001).]
Posted By: sparky Re: 100 A feeders - 05/16/01 10:54 PM
it would be at;
http://www.nfpa.org/Codes/National_Electrical_CodeR_NEC/Proposals/necpdf/A280-310.PDF

go down to about pg 65 ( Adobe Acrobat file)

points of interest;
Log 3908(accept) - to exempt 336-26 in T310-15(b)(6)
Log4200(reject) substantiation states;
[ "99' wording schizophrenic" ]
i sense the CMP's intent here, and a little frustration.....
Log 2895(reject) looks like a table for ampacity?>>>....

[Linked Image]
Posted By: golf junkie Re: 100 A feeders - 05/17/01 02:25 AM

Just what the heck am I supposed to do with 100A Sub panels? #3 CU THHN in pipe?


That's what we typically do. MLO sub-panel unless the sub is in a separate building.

I don't follow the other concerns, questions that lead to the 1/0 AL. We don't use AL for sub panels unless we are going underground.

GJ


[This message has been edited by golf junkie (edited 05-16-2001).]
Posted By: sparky Re: 100 A feeders - 05/17/01 08:54 PM
GJ;
the article in question is not entirely clear as to where #2 for 100A ,4/0 for 200A can be run in a dwelling.

the code had a 99' change, and is apparently going to have a change or two in 02'.

I'm confused on what has changed and why...

[Linked Image]
Posted By: sparky66wv Re: 100 A feeders - 05/18/01 03:37 AM
Another point, probably only a WV thing, but how am I supposed to pipe in and use 3 #3 THHN copper for the feeders AND a reduced ground and compete with those using only a #2 Al SE (NOT SER)?!??! Please realize that there is a major cost difference here...And please find me a loophole! (I'll use SER though...)

BTW I've lost 3 of 3 bids the past week, 2 due to "unfair" competition like I mentioned above... the third due to "Sticker shock"...
I don't mind it so bad when I actually bid against electricians...
Posted By: sparky Re: 100 A feeders - 05/18/01 11:15 AM
Virgil;
it's simply a matter of wording. don't go looking for #3 just yet, those other threads
,burning a hole thru cyberspace, have some big guns who are explaining the situation down to the punctuation marks.
(As well as some ROP's)
[Linked Image]
I'm presently doing an 8 meter pack 120/240 1 ph 3 wire, instead of 3 ph to take advantage of #2, on an 8-unit dwelling.....
( wanna job ?)

[Linked Image]
Posted By: sparky66wv Re: 100 A feeders - 05/18/01 02:02 PM
Yeah, but have we actually come to any conclusions? All I hear are code loops, man...

[Linked Image]

[This message has been edited by sparky66wv (edited 05-18-2001).]
Posted By: resqcapt19 Re: 100 A feeders - 05/18/01 02:59 PM
Sparky66
I think the only conclusion that would be valid is from your local AHJ or if someone requests a formal interpretation from the NFPA. Anything else is just opinion.
Don(resqcapt19)
Posted By: sparky66wv Re: 100 A feeders - 05/18/01 03:44 PM
The AHJ is my own conscience...

Unless a meter gets pulled (EI visit for the service only)

or I'm in L'burg (building inspector- don't get me started again!)
Posted By: Mike Re: 100 A feeders - 05/18/01 04:35 PM
Article 215-2(d)permits using article 310-15(b)(6) for sizing the feeder conductors in an individual dwelling unit. Article 310-15(b)(6) directs you to table 310-15(b)(6). Table 310-15(b)(6) doesn't mention SER insulation type. What is SER? Service entrance rated?
Posted By: sparky66wv Re: 100 A feeders - 05/18/01 04:39 PM
I don't know what it means, but SE is flat with 2 hots and a bare neutral (wrapped around the hots). SER has two hots, an insulated neutral and a reduced ground, and is round in shape, and the conductors are twisted together. Does R stand for "round" (that's how I remember it)

[This message has been edited by sparky66wv (edited 05-18-2001).]
Posted By: sparky66wv Re: 100 A feeders - 05/18/01 05:02 PM
215-2(d) is all well and good, but what if you're subbing off of a 200A panel?

215-2(d) applies if you have a #2 service entrance conductors, but most situations I'm talking about are truly sub panels being fed from a 200A Panel, although I started this thread with a 100A service and disco in mind. How does this change things here?

Someone somewhere mentioned using a 90A breaker and saying to heck with it...
Posted By: Mike Re: 100 A feeders - 05/18/01 05:43 PM
You size your service-entrance conductors per Table 310-15(b)(6). Why can't you size the 100 amp sub panel feeder conductors per Table 310-15(b)(6)? Me thinks some people are reading way too much into this example. Present company excluded! Like Don said, talk to the AHJ. IHMO the NEC Gods need to tie article 215-2(d) directly to Table 310-15(b)(6) and not article 310-15(b)(6). That would eliminate some, if not all, of the confusion. If it was me installing a sub panel, I would use Table 310-15(b)(6). [Linked Image]
Posted By: sparky Re: 100 A feeders - 05/18/01 09:15 PM
336-26 needs a ref to 310-15(b)(6) the same as 215-2(d) does ( as one ROP intends)
[Linked Image]
Posted By: sparky66wv Re: 100 A feeders - 05/19/01 09:23 AM
This thread has now been introduced to the big guns at the IAEI Bulletin Board . It looks like it's heating up there too! Let's see, that's four independent BB's on one unique topic at the same time! Wow! And coming to the same confusions I might add... [Linked Image]