100 A feeders #77224
05/16/01 12:53 PM
05/16/01 12:53 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
This has been beat to death in Mike Holt's BB and the DIY BB, but I'm still confused.

My supplier only carries #4/0 and #2 Al SE and SER cables... no other sizes. I realize that the supplier is not infallible...

Bidding around here is hard enough, I can't compete with the ignorant! Just what the heck am I supposed to do with 100A Sub panels? #3 CU THHN in pipe? #3-3 w/G Cu NMB cable (which is unavailable here)? The supplier is clueless, I just called him...

I've been through about $10K of lost bids this week mainly due to sticker shock...

Any venture capitalists out there? I promise not to spend frivolously like the tech companies did...

If not...Anybody wanna buy a slightly used Electrical Business? Just Kidding folks...

[Linked Image]


[This message has been edited by sparky66wv (edited 05-16-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
2017 / 2014 NEC & Related Books and Study Guides
Re: 100 A feeders #77225
05/16/01 01:12 PM
05/16/01 01:12 PM
M
Mike  Offline
Member
Joined: Feb 2001
Posts: 62
What wiring methods have you used in the past to install subpanels? You could order what you want to use and keep it in shop stock.

Re: 100 A feeders #77226
05/16/01 01:15 PM
05/16/01 01:15 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Oh... This is in reference to Table 310-15(b)(6),

100A feed through discos are unavailable here, we generally use load centers for discos (raintite). Does the feeder from the first load center (being used as a disco) to the second (being used as the main panel) qualify as a service feeder, or is it a sub feed??

BTW the EI passed a similar install just a few weeks ago... It was fed from a 200A panel with #2 SER (most around here would have used SE) and was obviously a sub panel.

Would using a main breaker in the sub panel instead of a MLO make any difference in the definition of the intended use of the cable?

This code loop could triple the price of a sub panel install for me and put me out of the competition, I can't be the only one complying with codes that "no one has heard of" around here... and expect to make money, or even get the jobs in the first place!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: 100 A feeders #77227
05/16/01 01:22 PM
05/16/01 01:22 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
There appears to be some controversy on whether or not #2 SER is allowed in a sub feed... Sorry I didn't make that part clear...
http://www.mikeholt.com/forum/Forum1/HTML/000545.html
http://forum.doityourself.com/showthread.php?threadid=58652



[This message has been edited by sparky66wv (edited 05-16-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: 100 A feeders #77228
05/16/01 04:51 PM
05/16/01 04:51 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
oh boy,
here we go...someone call for more tankers...
[Linked Image]
personally, i'm confused as to which code overrides which, and what changes have taken place ( or are going to..)

some articles to consider;
T310-15(b)(6) and whatever the 99' change was
338-4(a) brings you to;
336 A&B ends up in
336-26 , note the 60 deg deal...
110-14(c) honorable mention.....
T-310-16 why not....

[Linked Image]

Re: 100 A feeders #77229
05/16/01 05:34 PM
05/16/01 05:34 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Whoa... looks like that leaves us with a #1/0 Al Sub Feeder for 100A...

Steve or Bill... you got the ROP's on this?

[Linked Image] [Linked Image]

[This message has been edited by sparky66wv (edited 05-16-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: 100 A feeders #77230
05/16/01 06:54 PM
05/16/01 06:54 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
it would be at;
http://www.nfpa.org/Codes/National_Electrical_CodeR_NEC/Proposals/necpdf/A280-310.PDF

go down to about pg 65 ( Adobe Acrobat file)

points of interest;
Log 3908(accept) - to exempt 336-26 in T310-15(b)(6)
Log4200(reject) substantiation states;
[ "99' wording schizophrenic" ]
i sense the CMP's intent here, and a little frustration.....
Log 2895(reject) looks like a table for ampacity?>>>....

[Linked Image]

Re: 100 A feeders #77231
05/16/01 10:25 PM
05/16/01 10:25 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE

Just what the heck am I supposed to do with 100A Sub panels? #3 CU THHN in pipe?


That's what we typically do. MLO sub-panel unless the sub is in a separate building.

I don't follow the other concerns, questions that lead to the 1/0 AL. We don't use AL for sub panels unless we are going underground.

GJ


[This message has been edited by golf junkie (edited 05-16-2001).]

Re: 100 A feeders #77232
05/17/01 04:54 PM
05/17/01 04:54 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
GJ;
the article in question is not entirely clear as to where #2 for 100A ,4/0 for 200A can be run in a dwelling.

the code had a 99' change, and is apparently going to have a change or two in 02'.

I'm confused on what has changed and why...

[Linked Image]

Re: 100 A feeders #77233
05/17/01 11:37 PM
05/17/01 11:37 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Another point, probably only a WV thing, but how am I supposed to pipe in and use 3 #3 THHN copper for the feeders AND a reduced ground and compete with those using only a #2 Al SE (NOT SER)?!??! Please realize that there is a major cost difference here...And please find me a loophole! (I'll use SER though...)

BTW I've lost 3 of 3 bids the past week, 2 due to "unfair" competition like I mentioned above... the third due to "Sticker shock"...
I don't mind it so bad when I actually bid against electricians...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,902
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 9
Popular Topics(Views)
249,305 Are you busy
187,238 Re: Forum
176,605 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.008s) Memory: 1.0261 MB (Peak: 1.2004 MB) Zlib enabled. Server Time: 2018-09-20 11:37:40 UTC