I am pretty sure infrared heaters installed on outdoor patios must be figured at 125% and included on residential load calcs, is this correct?
Posted By: gfretwell

Re: Outdoor Patio Heating & Residential Load Calcs - 02/08/13 07:27 AM

They get computed at 100% on the load calc but the branch circuit gets sized at 125%.
Posted By: BigB

Re: Outdoor Patio Heating & Residential Load Calcs - 02/08/13 03:22 PM

OK thanks Greg
Posted By: gfretwell

Re: Outdoor Patio Heating & Residential Load Calcs - 02/08/13 07:03 PM

Depending on which method you use the bottom line may not end up being the whole load added with the heaters but the 100% is what you plug into the calculation.