Outdoor Patio Heating & Residential Load Calcs
#208721
02/08/13 01:42 AM
|
Joined: Mar 2004
Posts: 782
OP
Member
|
I am pretty sure infrared heaters installed on outdoor patios must be figured at 125% and included on residential load calcs, is this correct?
|
|
|
Re: Outdoor Patio Heating & Residential Load Calcs
[Re: BigB]
#208722
02/08/13 03:27 AM
|
Joined: Jul 2004
Posts: 9,575
Member
|
They get computed at 100% on the load calc but the branch circuit gets sized at 125%.
Greg Fretwell
|
|
|
Re: Outdoor Patio Heating & Residential Load Calcs
[Re: gfretwell]
#208726
02/08/13 11:22 AM
|
Joined: Mar 2004
Posts: 782
OP
Member
|
|
|
|
Re: Outdoor Patio Heating & Residential Load Calcs
[Re: BigB]
#208728
02/08/13 03:03 PM
|
Joined: Jul 2004
Posts: 9,575
Member
|
Depending on which method you use the bottom line may not end up being the whole load added with the heaters but the 100% is what you plug into the calculation.
Greg Fretwell
|
|
|
|
|