I recently moved-on from my old job and started working for another contractor here in New Jersey. During one of our morning discussions/ ball-breaking sessions, it was brought up that anti-shorts (redheads) are no longer required for MC cable. It was news to me. When was this "change" made to the code? Personally, I think this is bad for the industry and could only lead to more ground/ neutral shorts and possibly start fires.
What do you think?
[This message has been edited by ShockMe77 (edited 08-03-2005).]
My understanding is that it was never a requirement in the written language of the code, but may be a requirement in the manufacturer's specs (as they include several of them with the product).
Dave
Thanks Dave.
I'll bring that up next time it's discussed.
Makes sense to me!
Check out this thread,
https://www.electrical-contractor.net/ubb/Forum2/HTML/001320.html the links are out of date, but Iwire provides the NEMA bulletin in his post of 11-27-2003 at 08:21 AM.
Roger
[This message has been edited by Roger (edited 08-03-2005).]
Thanks for the clarification Roger. I finally looked up the difference between AC and MC. I'm using AC with the anti-short bushings.
Dave
Thanks Rog! I followed that link and read it all. I'm definitely going to still use the redheads just be on the safe side.
Ron
Followed the old thread, saw the comment about using a wrap of tape to secure them. I have stopped guys in the past from doing this because if you get enough tape on there the MC jacket is insulated from contact with the connector and remains unbonded. I had one guy doing ALL ends this way, meaning BOTH ends of a cable, leaving the jackets isolated.