#94619 08/03/05 07:07 PM
Joined: Jun 2005
Posts: 821
S
Member
I recently moved-on from my old job and started working for another contractor here in New Jersey. During one of our morning discussions/ ball-breaking sessions, it was brought up that anti-shorts (redheads) are no longer required for MC cable. It was news to me. When was this "change" made to the code? Personally, I think this is bad for the industry and could only lead to more ground/ neutral shorts and possibly start fires.

What do you think?

[This message has been edited by ShockMe77 (edited 08-03-2005).]

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#94620 08/03/05 08:10 PM
Joined: May 2005
Posts: 706
T
Member
My understanding is that it was never a requirement in the written language of the code, but may be a requirement in the manufacturer's specs (as they include several of them with the product).

Dave

#94621 08/03/05 08:32 PM
Joined: Jun 2005
Posts: 821
S
Member
Thanks Dave.

I'll bring that up next time it's discussed.

Makes sense to me!

#94622 08/03/05 08:38 PM
Joined: May 2002
Posts: 1,716
R
Member
Check out this thread,
https://www.electrical-contractor.net/ubb/Forum2/HTML/001320.html

the links are out of date, but Iwire provides the NEMA bulletin in his post of 11-27-2003 at 08:21 AM.

Roger

[This message has been edited by Roger (edited 08-03-2005).]

#94623 08/03/05 11:31 PM
Joined: May 2005
Posts: 706
T
Member
Thanks for the clarification Roger. I finally looked up the difference between AC and MC. I'm using AC with the anti-short bushings.

Dave

#94624 08/04/05 09:16 PM
Joined: Jun 2005
Posts: 821
S
Member
Thanks Rog! I followed that link and read it all. I'm definitely going to still use the redheads just be on the safe side.

Ron

#94625 08/06/05 01:51 PM
Joined: Jun 2005
Posts: 124
P
Member
Followed the old thread, saw the comment about using a wrap of tape to secure them. I have stopped guys in the past from doing this because if you get enough tape on there the MC jacket is insulated from contact with the connector and remains unbonded. I had one guy doing ALL ends this way, meaning BOTH ends of a cable, leaving the jackets isolated.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 806
Joined: October 2004
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
303,014 Are you busy
232,124 Re: Forum
216,776 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5