#99222 - 07/31/06 01:25 PM Condulet Support
rocha12 Offline
Junior Member
Registered: 05/09/06
Posts: 5
Article 314.16.C.2 states that a conduit body "shall be supported in a rigid and secure manner" yet 314.22.E says you can hang a condulet from an EMT pipe run. I don't believe that can be considered a "rigid and secure manner" Ideas welcome
Top
2017 / 2014 NEC & Related Books and Study Guides
#99223 - 07/31/06 01:33 PM Re: Condulet Support
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
My Idea is your thinking about it to much.

If you place EMT supports close to both sides of the conduit body it will be rigidly supported.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99224 - 07/31/06 01:54 PM Re: Condulet Support
rocha12 Offline
Junior Member
Registered: 05/09/06
Posts: 5
But the code allows up to 3' on either side of the condulet. It's not 12" any more
Top
#99225 - 07/31/06 02:03 PM Re: Condulet Support
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Yes the code allows 36" but along with the EMT support requirements we must follow 314.16(C)(2).

It is a judgment call as to if 36" is close enough to meet 314.16(C)(2).

I am likely to support both sides of an LB within 12" on smaller EMT, on 4" EMT 36" will normally do fine.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99226 - 07/31/06 02:09 PM Re: Condulet Support
rocha12 Offline
Junior Member
Registered: 05/09/06
Posts: 5
I agree! How do you feel about drilling the condulet and mounting it to strut?
Top
#99227 - 07/31/06 02:52 PM Re: Condulet Support
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Rocha12
I have seen that done, and I asked the magic question......'where does the mfg instructions say that is OK??'

Haven't seen an answer yet.

John

PS: Welcome to the forum; where are you located??

[This message has been edited by HotLine1 (edited 07-31-2006).]
_________________________
John
Top
#99228 - 07/31/06 02:55 PM Re: Condulet Support
rocha12 Offline
Junior Member
Registered: 05/09/06
Posts: 5
I'm an electrical inspector at Lawrence Livermore Lab in Livermore CA.
I am also a contractor B & C10
Top
#99229 - 07/31/06 03:07 PM Re: Condulet Support
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I have drilled a few conduit bodies in some instances where I wanted to add support. Mostly due to the pulling that I would be doing later.


I have also drilled drain holes in conduit bodies.

We are required to 'arrange to drain'.

IMO a small hole in conduit body can do this.

Is it it A-OK with the manufactures?

I doubt they say so publicly.

But come on we drill enclosures all the time for mounting or entering.


JMO, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99230 - 08/01/06 04:50 AM Re: Condulet Support
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Bob:
I really know what you mean; been there, done that.

John
_________________________
John
Top
#99231 - 08/01/06 09:24 AM Re: Condulet Support
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I like the idea of rigidly mounting condolets too. I agree it is not necessary but it does give a lot more rigid installation than the one holers when a future user starts doing chin ups from the raceways.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals