Posted By: rocha12 Condulet Support - 07/31/06 08:25 PM
Article 314.16.C.2 states that a conduit body "shall be supported in a rigid and secure manner" yet 314.22.E says you can hang a condulet from an EMT pipe run. I don't believe that can be considered a "rigid and secure manner" Ideas welcome
Posted By: iwire Re: Condulet Support - 07/31/06 08:33 PM
My Idea is your thinking about it to much. [Linked Image]

If you place EMT supports close to both sides of the conduit body it will be rigidly supported.
Posted By: rocha12 Re: Condulet Support - 07/31/06 08:54 PM
But the code allows up to 3' on either side of the condulet. It's not 12" any more
Posted By: iwire Re: Condulet Support - 07/31/06 09:03 PM
Yes the code allows 36" but along with the EMT support requirements we must follow 314.16(C)(2).

It is a judgment call as to if 36" is close enough to meet 314.16(C)(2).

I am likely to support both sides of an LB within 12" on smaller EMT, on 4" EMT 36" will normally do fine.

Bob
Posted By: rocha12 Re: Condulet Support - 07/31/06 09:09 PM
I agree! How do you feel about drilling the condulet and mounting it to strut?
Posted By: HotLine1 Re: Condulet Support - 07/31/06 09:52 PM
Rocha12
I have seen that done, and I asked the magic question......'where does the mfg instructions say that is OK??'

Haven't seen an answer yet.

John

PS: Welcome to the forum; where are you located??

[This message has been edited by HotLine1 (edited 07-31-2006).]
Posted By: rocha12 Re: Condulet Support - 07/31/06 09:55 PM
I'm an electrical inspector at Lawrence Livermore Lab in Livermore CA.
I am also a contractor B & C10
Posted By: iwire Re: Condulet Support - 07/31/06 10:07 PM
I have drilled a few conduit bodies in some instances where I wanted to add support. Mostly due to the pulling that I would be doing later.


I have also drilled drain holes in conduit bodies.

We are required to 'arrange to drain'.

IMO a small hole in conduit body can do this.

Is it it A-OK with the manufactures?

I doubt they say so publicly.

But come on we drill enclosures all the time for mounting or entering. [Linked Image]


JMO, Bob
Posted By: HotLine1 Re: Condulet Support - 08/01/06 11:50 AM
Bob:
I really know what you mean; been there, done that.

John
Posted By: gfretwell Re: Condulet Support - 08/01/06 04:24 PM
I like the idea of rigidly mounting condolets too. I agree it is not necessary but it does give a lot more rigid installation than the one holers when a future user starts doing chin ups from the raceways.