The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#96912 - 01/07/06 04:11 PM Table 210.21 (B) (3) Interpretation
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
According to this table for receptacle ratings can you run a 20 amp circuit and use 15 amp rated receptacles on it? It says...
ciruit rating 20 = receptacle rating 15 or 20. Am I looking at this right or do I have to use 20 amp receptacles?

Top
2014 / 2011 NEC & Related Books and Study Guides
#96913 - 01/07/06 04:56 PM Re: Table 210.21 (B) (3) Interpretation
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
As long as there is more than one receptacle on the circuit, a 15 amp receptacle can be installed on a 20-amp circuit. Remember that a duplex receptacle is 2 receptacles. Therefore, a 15-amp duplex can be installed on a 20-amp ckt.

Top
#96914 - 01/07/06 07:17 PM Re: Table 210.21 (B) (3) Interpretation
AllClear Offline
Member

Registered: 08/22/05
Posts: 44
Loc: Belmond Iowa US
The Heading For this Table Is

"Maximum Cord-and-Plug Connected Load to Receptacle"

After I Looked it Up I was left wondering about it also. The Max for a 15A Recep. is 12 amps. Am I In Violation if I plug in Something that Draws 13 amps into a 15A Recpt? Like my Vaccume Cleaner, It says 13 amps in big bold letters right on the front of it.
_________________________
It's Not The Fall That Kills You...
It's That Sudden Stop At The End

Top
#96915 - 01/07/06 07:56 PM Re: Table 210.21 (B) (3) Interpretation
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
That should be controlled by the NRTL that listed it. If it was really a 13a load it should have a 5-20 plug ... but that is far from certain. I have a U/L listed 1650w smoker with a 5-15 plug.
It has tripped breakers and burned up plenty of cheap receptacles before I inherited it.
I use it on a dedicated spec grade 5-20 with no problems.
_________________________
Greg Fretwell

Top
#96916 - 01/08/06 04:30 AM Re: Table 210.21 (B) (3) Interpretation
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Guys,

The inquiry is to Table 210.21(B)(3), not 210.21(B)(2)

Top
#96917 - 01/08/06 07:31 PM Re: Table 210.21 (B) (3) Interpretation
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
REDSY,
So I can install 15 amp receptacles on my new 20 amp branch circuit? Thanks for the reply by the way. Also, maybe someone knows the answer to this question. In a room additon I'm working on one whole 8 foot wall is going to be cabinets surrounding a window. Am I still required to install a receptacles somewhere in the cabinets to keep with the dwelling unit every 6 feet rule? Thanks

Top
#96918 - 01/08/06 08:26 PM Re: Table 210.21 (B) (3) Interpretation
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
What is the "every 6' rule"?

I hope you mean every 12' rule.
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top
#96919 - 01/09/06 08:15 AM Re: Table 210.21 (B) (3) Interpretation
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
No, according to 210.52(A)(1), "receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more that 6 ft from a receptacle outlet". I understand you are talking about installing them 12 feet apart so there is only 6 feet to the middle. But what do you do when one whole wall is taken up with cabinets?

Top
#96920 - 01/09/06 08:30 AM Re: Table 210.21 (B) (3) Interpretation
sabrown Offline
Member

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
Ask your AHJ. If they consider cabinets to be like a closet then no you would not have to. But I can not picture your exact situation. The AHJ should be asking if the cabinets are permenant, floor to ceiling, or if any counter space. Then they would interpret things as best they can.

Consider the use of the cabinets and their design, you may want them anyway. I would recommend installing at least per wall requirement just because it is handy. When I installed my permenent library shelves, I installed receptacles accessible within them and I have found myself using them on occasion.

Shane

Top
#96921 - 01/09/06 09:56 AM Re: Table 210.21 (B) (3) Interpretation
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Shane that is the real question. Is a receptacle inside a cabinet considered one of the 210.52(A)(1) receptacles?
I would say yes. An entertainment center that runs the length of the wall is a good example.
_________________________
Greg Fretwell