The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Did you know?
by Admin
37 minutes 25 seconds ago
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 81 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94209 - 07/18/05 11:11 AM pipe fill
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
will a 6-3 romex fit in a 3/4" pvc?
not sure how to calculate the 53% single conductor.

thanx,
h2o
Top
2017 / 2014 NEC & Related Books and Study Guides
#94210 - 07/18/05 01:19 PM Re: pipe fill
George Offline
Member
Registered: 02/23/02
Posts: 380
I believe for Southern Wire Corp the diameter is .683".
Top
#94211 - 07/18/05 01:47 PM Re: pipe fill
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
Take the largest diameter across the cable. Calculate the cross section area is if the cable were round with this diameter. (PI*D^2)/4

Divide this by the internal area of the conduit. If the answer is less than 0.53, you are good to go.

-Jon
Top
#94212 - 07/18/05 05:09 PM Re: pipe fill
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 132
Loc: MA, USA
Looks like you need to go to 1"

assuming .683 diameter:

Area = Pi*r^2 = 3.14*.3415^2 = .366
assuming sched 40 PVC:
max allowable 53% fill area for 3/4" is .269 (too small)
max allowable 53% fill area for 1" is
.441 (that'll work)
Top
#94213 - 07/18/05 11:04 PM Re: pipe fill
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
thanx guys....