The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
2 registered (HotLine1, gfretwell), 304 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94209 - 07/18/05 11:11 AM pipe fill
watersparkfalls Offline

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
will a 6-3 romex fit in a 3/4" pvc?
not sure how to calculate the 53% single conductor.


2014 / 2011 NEC & Related Books and Study Guides
#94210 - 07/18/05 01:19 PM Re: pipe fill
George Offline

Registered: 02/23/02
Posts: 380
I believe for Southern Wire Corp the diameter is .683".

#94211 - 07/18/05 01:47 PM Re: pipe fill
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Take the largest diameter across the cable. Calculate the cross section area is if the cable were round with this diameter. (PI*D^2)/4

Divide this by the internal area of the conduit. If the answer is less than 0.53, you are good to go.


#94212 - 07/18/05 05:09 PM Re: pipe fill
Electric Ian Offline

Registered: 02/10/04
Posts: 132
Loc: MA, USA
Looks like you need to go to 1"

assuming .683 diameter:

Area = Pi*r^2 = 3.14*.3415^2 = .366
assuming sched 40 PVC:
max allowable 53% fill area for 3/4" is .269 (too small)
max allowable 53% fill area for 1" is
.441 (that'll work)

#94213 - 07/18/05 11:04 PM Re: pipe fill
watersparkfalls Offline

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
thanx guys....