ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
2 members (Scott35, gfretwell), 269 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#94209 07/18/05 02:11 PM
Joined: Mar 2005
Posts: 240
Member
will a 6-3 romex fit in a 3/4" pvc?
not sure how to calculate the 53% single conductor.

thanx,
h2o

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#94210 07/18/05 04:19 PM
Joined: Feb 2002
Posts: 375
G
Member
I believe for Southern Wire Corp the diameter is .683".

#94211 07/18/05 04:47 PM
Joined: Sep 2003
Posts: 650
W
Member
Take the largest diameter across the cable. Calculate the cross section area is if the cable were round with this diameter. (PI*D^2)/4

Divide this by the internal area of the conduit. If the answer is less than 0.53, you are good to go.

-Jon

#94212 07/18/05 08:09 PM
Joined: Feb 2004
Posts: 133
E
Member
Looks like you need to go to 1"

assuming .683 diameter:

Area = Pi*r^2 = 3.14*.3415^2 = .366
assuming sched 40 PVC:
max allowable 53% fill area for 3/4" is .269 (too small)
max allowable 53% fill area for 1" is
.441 (that'll work)

#94213 07/19/05 02:04 AM
Joined: Mar 2005
Posts: 240
Member
thanx guys....

h2o