#94070 - 07/05/05 08:33 PM 50 amp hot tub
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
can you use nm 8-3 to feed a 50 amp hot tub?
Top
2017 / 2014 NEC & Related Books and Study Guides
#94071 - 07/05/05 09:21 PM Re: 50 amp hot tub
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think not. NM is not one of the approved wiring methods in 680 part II. I also could have problems with the ampacity, based on the nameplate rating of the spa and mfg instructions. 8ga is only good for 40a in the 60c column.
_________________________
Greg Fretwell
Top
#94072 - 07/06/05 04:16 AM Re: 50 amp hot tub
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg- The question is not stating whether it is an indoor or outdoor spa. 680.42 and 680.43 come into play here.
_________________________
George Little
Top
#94073 - 07/06/05 06:30 AM Re: 50 amp hot tub
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
it is an outdoor hot tub
Top
#94074 - 07/06/05 01:44 PM Re: 50 amp hot tub
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Are you asking if you can run NM outside to a hot tub?
Top
#94075 - 07/06/05 02:59 PM Re: 50 amp hot tub
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Romex (type NM) is allowed in the interior of a one family dwelling or the interior of a structure associated with a one family dwelling...

But read the instructions with the tub and labels at the control box behind the skirt of the tub. Some require a full size EGC to be run with the circuit conductors...

shortcircuit
Top
#94076 - 07/06/05 03:25 PM Re: 50 amp hot tub
boggerbutt2454 Offline
Member
Registered: 02/27/05
Posts: 44
Loc: Concord NC USA
Shorties right read your Manufacture's manual most spa manufacture's will put min. wire size and I've found more times tahn not it is a #6 copper, but check your manual. If customer doesn' know call dealer they bought it from.
Top
#94077 - 07/06/05 03:38 PM Re: 50 amp hot tub
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If NM is in fact appropriate 8 AWG NM can not be used above 40 amps.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#94078 - 07/06/05 11:22 PM Re: 50 amp hot tub
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
no i am not asking if i can run the nm outside. just wondering if i can calculate hot tub as a motor to use smaller wire.

any thoughts against using 6-3 aluminum?
Top
#94079 - 07/07/05 09:52 AM Re: 50 amp hot tub
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
A spa is a combination load with a significant part that is a "toaster wire" heater. The answer is in the manufacturer's instructions unless you want to start reading nameplate ratings and calculating.
You are still stuck in the 60c column with Romex.
_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals