#94070 07/05/05 11:33 PM
can you use nm 8-3 to feed a 50 amp hot tub?
#94071 07/06/05 12:21 AM
I think not. NM is not one of the approved wiring methods in 680 part II. I also could have problems with the ampacity, based on the nameplate rating of the spa and mfg instructions. 8ga is only good for 40a in the 60c column.
#94072 07/06/05 07:16 AM
Greg- The question is not stating whether it is an indoor or outdoor spa. 680.42 and 680.43 come into play here.
George Little
#94073 07/06/05 09:30 AM
it is an outdoor hot tub
#94074 07/06/05 04:44 PM
Are you asking if you can run NM outside to a hot tub?
#94075 07/06/05 05:59 PM
Romex (type NM) is allowed in the interior of a one family dwelling or the interior of a structure associated with a one family dwelling...
But read the instructions with the tub and labels at the control box behind the skirt of the tub. Some require a full size EGC to be run with the circuit conductors...
shortcircuit
#94076 07/06/05 06:25 PM
Shorties right read your Manufacture's manual most spa manufacture's will put min. wire size and I've found more times tahn not it is a #6 copper, but check your manual. If customer doesn' know call dealer they bought it from.
#94077 07/06/05 06:38 PM
If NM is in fact appropriate 8 AWG NM can not be used above 40 amps.
#94078 07/07/05 02:22 AM
no i am not asking if i can run the nm outside. just wondering if i can calculate hot tub as a motor to use smaller wire.
any thoughts against using 6-3 aluminum?
#94079 07/07/05 12:52 PM
A spa is a combination load with a significant part that is a "toaster wire" heater. The answer is in the manufacturer's instructions unless you want to start reading nameplate ratings and calculating.
You are still stuck in the 60c column with Romex.