ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,865 Are you busy
166,747 Re: Forum
160,870 Need opinion
Who's Online Now
0 registered members (), 82 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#93102 - 05/03/05 11:08 AM Length of GEC  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Is there a max length for this?

Reason for the question is this:

From a SDS, 480x208/120Y transformer, I need to go to building steel with the GEC, but the transformer is in the middle of the floor.

Is there a max length that it can be, and does it have to be protected from damage in conduit, or can it be supported, say with ty-wraps, to the feeder conduit?

Dnk....


2017 / 2014 NEC & Related Books and Study Guides

#93103 - 05/03/05 01:24 PM Re: Length of GEC  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I'm not seeing any length limitations. As for does it require physical protection-(250.64(B) It would depend on the size of conductor, #8 needs to be in conduit, #6 can go in without conduit as long as it follows the surface of the building, #4 needs protection if subject to severe physical damage-(Hi-Lo type setting), and as to ty-wraping it to the feeder conduit. Someone has to make the call that it is "functionally associated" I'd make the call in my jurisdiction and probably say "No".


George Little

#93104 - 05/03/05 09:14 PM Re: Length of GEC  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
It needs to go to the "nearest" electrode. I would double check to see if the steel is actually part of the electrode system before actually going there. Would not be cool it it were not. As you would end up with a floating neutral and a kinda live piece of building steel, or being dependant on any ground that may have come over with the feed.

If the nearest electrode were a main panel, and you were feeding from it, I don't see why the GEC could not be run IN the feed conduit, as long as it were sized right for the secondary. And it is an exception to at least the 2002 NEC in 250.30 (4) to come from the main. Its the best place anyway, reguardless of "nearest" IMO.


Mark Heller
"Well - I oughta....." -Jackie Gleason

#93105 - 05/03/05 09:37 PM Re: Length of GEC  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
e57- If he's using a metal raceway he needs to watch his bonding on both ends 250.92(A)(3) and/or 250.64(E)


George Little


Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7580 MB (Peak: 0.8914 MB) Zlib enabled. Server Time: 2017-03-30 14:38:36 UTC