The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92993 - 04/22/05 01:04 PM Optional Method Calc
electcontrctr Offline
Member

Registered: 04/07/05
Posts: 15
Loc: Fairbanks, AK USA
Hi,
What is the optional method for a load calc? Can this be used on a sub panel?

I used an online calculator and got the following:

General Light and Receptacle Load
1308sqft x 3VA = 3924VA
________________________________________
Small Appliance Circuits Load
2 x 1500VA = 3000VA
________________________________________
Laundry Branch Circuit(s) Load
1 x 1500VA = 1500VA
________________________________________
Total General Load Less Demand
sum of above less T220.11 demand
sum of above = 8424VA
first 3000 at 100 % = 3000
next 117,000 at 35% = 1898
remainder at 25% = 0
sum less demand = 4898VA
________________________________________
Fastened In Place Appliances Load
Disposal = 1176VA
Garage Door = 1000VA
Dish Washer = 1600VA
Attic Fan = 700VA
Microwave = 975VA
sum less 75% demand = 4088VA
________________________________________
Clothes Dryer Circuit(s)Load
Total dryer circuit(s) load = 0VA
________________________________________
Cooking Appliance(s) Load
Range 9.5kVA
T220.19 Column A = 8kVA
T220.19 Column B = 0kVA
T220.19 Column C = 0kVA
Total calc.d range load = 8kVA
________________________________________
Heating or Air-Conditioning Load
Air Conditioner = 4240VA
________________________________________
Largest Motor Load
25% of largest motor = 1000VA
________________________________________
Total Computed Load
22226 Volt-Amps
________________________________________
Computed Amperage
22226 divided by 240 = 93Amps

-------------------------------------

Is there anyway to get this down so I could connect a dryer to it?

Thanks

Bradley

Top
2014 / 2011 NEC & Related Books and Study Guides
#92994 - 04/22/05 03:10 PM Re: Optional Method Calc
markp Offline
Member

Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
See NEC 220.30. This usually comes in smaller than the standard calculation. You also must have a service or feeder rated at 100A or more in order to use it (so I think you're OK with a 100A subpanel if its on a 100A feeder).

When I run your numbers with the optional calculation, I get 90 amps including a dryer. This was based on:
3.92 KVA living space
4.5 KVA small appliance circuits
5 KVA Dryer
9.5 KVA range
1.6 KVA Dish Washer
.98 KVA Microwave
1.18 KVA DIsposal
1 KVA Garage Door Motor
0.7 KVA Attic Fan

This comes to 28.38 KVA. The first 10 KVA are 100% and the remaining is 40%. So this reduces the load to 17.35 KVA. Then we add the Air Conditioner at 4.24 KVA giving a total of 21.6 KVA which is 90A.

About the only thing I can comment on your standard calculation you included is what air conditioner amp rating did you use? Was it MCA or FLA+RLA? If its MCA, that already has the 25% factor for the largest motor so you can remove that item from the calculation.
_________________________
Mark
Kent, WA

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals