Optional Method Calc - 04/22/05 08:04 PM
Hi,
What is the optional method for a load calc? Can this be used on a sub panel?
I used an online calculator and got the following:
General Light and Receptacle Load
1308sqft x 3VA = 3924VA
________________________________________
Small Appliance Circuits Load
2 x 1500VA = 3000VA
________________________________________
Laundry Branch Circuit(s) Load
1 x 1500VA = 1500VA
________________________________________
Total General Load Less Demand
sum of above less T220.11 demand
sum of above = 8424VA
first 3000 at 100 % = 3000
next 117,000 at 35% = 1898
remainder at 25% = 0
sum less demand = 4898VA
________________________________________
Fastened In Place Appliances Load
Disposal = 1176VA
Garage Door = 1000VA
Dish Washer = 1600VA
Attic Fan = 700VA
Microwave = 975VA
sum less 75% demand = 4088VA
________________________________________
Clothes Dryer Circuit(s)Load
Total dryer circuit(s) load = 0VA
________________________________________
Cooking Appliance(s) Load
Range 9.5kVA
T220.19 Column A = 8kVA
T220.19 Column B = 0kVA
T220.19 Column C = 0kVA
Total calc.d range load = 8kVA
________________________________________
Heating or Air-Conditioning Load
Air Conditioner = 4240VA
________________________________________
Largest Motor Load
25% of largest motor = 1000VA
________________________________________
Total Computed Load
22226 Volt-Amps
________________________________________
Computed Amperage
22226 divided by 240 = 93Amps
-------------------------------------
Is there anyway to get this down so I could connect a dryer to it?
Thanks
Bradley
What is the optional method for a load calc? Can this be used on a sub panel?
I used an online calculator and got the following:
General Light and Receptacle Load
1308sqft x 3VA = 3924VA
________________________________________
Small Appliance Circuits Load
2 x 1500VA = 3000VA
________________________________________
Laundry Branch Circuit(s) Load
1 x 1500VA = 1500VA
________________________________________
Total General Load Less Demand
sum of above less T220.11 demand
sum of above = 8424VA
first 3000 at 100 % = 3000
next 117,000 at 35% = 1898
remainder at 25% = 0
sum less demand = 4898VA
________________________________________
Fastened In Place Appliances Load
Disposal = 1176VA
Garage Door = 1000VA
Dish Washer = 1600VA
Attic Fan = 700VA
Microwave = 975VA
sum less 75% demand = 4088VA
________________________________________
Clothes Dryer Circuit(s)Load
Total dryer circuit(s) load = 0VA
________________________________________
Cooking Appliance(s) Load
Range 9.5kVA
T220.19 Column A = 8kVA
T220.19 Column B = 0kVA
T220.19 Column C = 0kVA
Total calc.d range load = 8kVA
________________________________________
Heating or Air-Conditioning Load
Air Conditioner = 4240VA
________________________________________
Largest Motor Load
25% of largest motor = 1000VA
________________________________________
Total Computed Load
22226 Volt-Amps
________________________________________
Computed Amperage
22226 divided by 240 = 93Amps
-------------------------------------
Is there anyway to get this down so I could connect a dryer to it?
Thanks