#90710 - 12/08/04 08:17 AM Fire pump feeder & disconnect
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Fire pump 20hp & booster pump 3/4 hp.460volt3phase

20hp=27amps LRC=145 amps
3/4 hp=1.6 amps LRC 12.5 amps
Disconnect Size 145 +12.5=157.5
240.6 next size up 175amps
175amp disconnect switch
The way I read it from the fire pump locked rotor sized disconnect switch to fire pump controller wire sized at 125 %
27plus 1.6=28.6x125%=28.6
according to the code 175 amp disconnect switch with 30 amp wire from switch to fire pump controller then to the mtr. code handbook 2002 pages 975-976.
Please comment . Thank u
Top
2017 / 2014 NEC & Related Books and Study Guides
#90711 - 12/08/04 04:30 PM Re: Fire pump feeder & disconnect
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Yooper- I see you got it right. You must have had a good teacher
_________________________
George Little
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 81 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals