The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90710 - 12/08/04 08:17 AM Fire pump feeder & disconnect
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
Fire pump 20hp & booster pump 3/4 hp.460volt3phase

20hp=27amps LRC=145 amps
3/4 hp=1.6 amps LRC 12.5 amps
Disconnect Size 145 +12.5=157.5
240.6 next size up 175amps
175amp disconnect switch
The way I read it from the fire pump locked rotor sized disconnect switch to fire pump controller wire sized at 125 %
27plus 1.6=28.6x125%=28.6
according to the code 175 amp disconnect switch with 30 amp wire from switch to fire pump controller then to the mtr. code handbook 2002 pages 975-976.
Please comment . Thank u

2014 / 2011 NEC & Related Books and Study Guides
#90711 - 12/08/04 04:30 PM Re: Fire pump feeder & disconnect
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Yooper- I see you got it right. You must have had a good teacher