ECN Forum
Posted By: Yoopersup Fire pump feeder & disconnect - 12/08/04 04:17 PM
Fire pump 20hp & booster pump 3/4 hp.460volt3phase

20hp=27amps LRC=145 amps
3/4 hp=1.6 amps LRC 12.5 amps
Disconnect Size 145 +12.5=157.5
240.6 next size up 175amps
175amp disconnect switch
The way I read it from the fire pump locked rotor sized disconnect switch to fire pump controller wire sized at 125 %
27plus 1.6=28.6x125%=28.6
according to the code 175 amp disconnect switch with 30 amp wire from switch to fire pump controller then to the mtr. code handbook 2002 pages 975-976.
Please comment . Thank u
Posted By: George Little Re: Fire pump feeder & disconnect - 12/09/04 12:30 AM
Yooper- I see you got it right. You must have had a good teacher [Linked Image]
© ECN Electrical Forums