The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Trumpy 6
Who's Online
1 registered (brsele), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89903 - 10/23/04 06:20 PM Cold water bond
dmattox Offline
Member

Registered: 10/20/04
Posts: 267
Loc: Anaheim, CA
On a job I am doing, the building inspector(not the electrical inspector) is requiring us to bond to the cold water even though it is PVC in the ground. The only requirement that I know of for a cold water is to bond it as a grounding electrode, but since its PVC that doesn't apply. Is there any section of the NEC that just requires cold water to be bonded?

Worst part is that this is actually 4 suites, and he wants all the suites bonded. We are bonded to building steel and the ufer, which satifies grounding electrode requirements of the NEC.

Top
2014 / 2011 NEC & Related Books and Study Guides
#89904 - 10/23/04 06:31 PM Re: Cold water bond
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
250.53 requires bonding when the water pipe is used as a grounding electrode.

250.104 requires bonding of the water pipe in the event it becomes energized within the residence.
_________________________
Ron

Top
#89905 - 10/23/04 08:07 PM Re: Cold water bond
dmattox Offline
Member

Registered: 10/20/04
Posts: 267
Loc: Anaheim, CA
ah, never noticed 250.104. Thanks Ron.