#89678 - 10/12/04 02:29 PM Insulated Neutral from SE
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
Is it not allowable to use an unisulated neutral in the portion of the sec's that are overhead or undeground?

I have a 200A 120/240 VAC Main Panel mounted on a pole..the feeder from the 200A main to the house is a 4/0 3 COND AL URD...2 insulated and one bare conductor (neut). w/ground rod at house..As far as I know this is a legal installation isn't it?

an insulated neutral is only required past the first OCPD EXCEPT where feed from a separate location like another building or pole?

i am getting old...so my memory is not working as good as it used to..

Thanks for any replies

Mustang
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#89679 - 10/12/04 03:12 PM Re: Insulated Neutral from SE
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
as long as the underground AL conductor meets the requirements of 230-30 EX.(D), I'd say yes, but I wouldn't put AL in the ground bare. What kind of URD is this? all the stuff I use has an insulated nuetral.
Top
#89680 - 10/12/04 04:04 PM Re: Insulated Neutral from SE
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
thanks for the reply. The cable looks as if it is a TRIPLEX that has been placed in the ground. I called it URD but I bet it is a TRI-PLEX XLPE.

I am planning to replace the feeder with a insulated neutral using URD (insulated neutral marked with yellow stripe).

I have seen the results of placing AL in direct contact with the earth...you end up with a white powder that loses continuity...

i inherited the job from the HO's cousin..

it looks like a 1st year apprentice took on more than he could chew..

as always, thanks for the replies..

-regards

Mustang
_________________________
Electricity has no respect for ignorance!
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals