Running 1" #40pvc 3' above grade leval attach to the front of the house in a horizontal way for about 40'. Not subject to vehicles. Will this violate 347-3c (1999 code for NY)
Top
2017 / 2014 NEC & Related Books and Study Guides
#87161 - 01/26/04 07:26 PM Re: Physical Damage #40 PVC
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
"Subject to physical damage" is a term that only the inspector can answer....
_________________________
Ryan Jackson,
Salt Lake City
Top
#87162 - 01/27/04 06:30 AM Re: Physical Damage #40 PVC
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
Another point to consider besides protection is expansion in hot weather. This will be a factor with a 40ft. run. I have seen pvc in horizontal runs with sags between supports even when placed the required distance apart. Use metallic conduit IMO.
_________________________
John
Top
#87163 - 01/27/04 07:03 AM Re: Physical Damage #40 PVC
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
PVC is great for your application. Just place the straps every foot or two, and the sag will not be noticable. Runs of more than 6-7 feet may have problems with expansion that would pull the fittings apart. If you come and go at the ends with a 90 degree, expansion will be taken up by the sweep, thereby avoiding an expansion sleeve. Lightly sand, and paint the PVC and it will blend into the siding on the house.
_________________________
Earl
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals