by NORCAL - 03/19/24 05:11 PM
1 members (Scott35), 278 guests, and 16 robots.
#87160 01/26/04 09:42 PM
Z
Zapper Offline OP
Running 1" #40pvc 3' above grade leval attach to the front of the house in a horizontal way for about 40'. Not subject to vehicles. Will this violate 347-3c (1999 code for NY)
#87161 01/26/04 11:26 PM
"Subject to physical damage" is a term that only the inspector can answer....
Ryan Jackson,
Salt Lake City
#87162 01/27/04 10:30 AM
Another point to consider besides protection is expansion in hot weather. This will be a factor with a 40ft. run. I have seen pvc in horizontal runs with sags between supports even when placed the required distance apart. Use metallic conduit IMO.
#87163 01/27/04 11:03 AM
PVC is great for your application. Just place the straps every foot or two, and the sag will not be noticable. Runs of more than 6-7 feet may have problems with expansion that would pull the fittings apart. If you come and go at the ends with a 90 degree, expansion will be taken up by the sweep, thereby avoiding an expansion sleeve. Lightly sand, and paint the PVC and it will blend into the siding on the house.
Earl