If an outdoor residential spa has a built in GFI, does it need a GFI breaker at the Panel feeding it? Does it need a disconnect near the spa when the panel is not in with site?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
2017 / 2014 NEC & Related Books and Study Guides
#86935 - 12/24/03 08:46 AM Re: SPA / GFI
dannynova Offline
Member
Registered: 12/22/03
Posts: 18
Loc: new york
according to 680-40 for outdoor spas it sends you to 680 parts A and B. 680-12 states that a disconnecting means shall be provided and accessible within sight of all pools, spas, and hot tubs and shall be at least 5 feet from the wall. As for the gfi requirement, in my area a gfci breaker is required but I cant find the article. I dont know if this is a local thing or in the nec. hope this helps.
Top
#86936 - 12/24/03 08:56 AM Re: SPA / GFI
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Yeah, I couldn't find the GFI requirement either. Thanks for your help.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#86937 - 12/24/03 09:54 AM Re: SPA / GFI
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Check out 680.44. If I'm not mistaken, a listed spa package with integral GFCI protection is permitted without GFCI protection on the branch circuit or the outlet serving the spa.
_________________________
Earl
Top
#86938 - 12/24/03 10:26 AM Re: SPA / GFI
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
the disco is something that needs to be within sight of the motor, as some tub motors are not intergral to the tub ( as in commercial settings) an E-stop for the serving motor is to be placed within sight of the tub. (from the hip, this might be 680.41)

isn't it interesting that , a permanent hardwired pool should not require a GFI , where most hot tubs & spas are listed for them?

must be something to do with the bonding eh?

~S~
Top
#86939 - 12/24/03 10:30 AM Re: SPA / GFI
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Yep, you would think an in-ground pool would need a GFI for the pump motor. The pool light has one.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals