The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 225 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86587 - 11/13/03 05:29 AM breaker trip
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Can some explain the current fault conditions.I was explaining to a guy about inrush current on breaker being more than breaker set point for a short time period before it trips.I really don`t feel I`ve done a good job explaining it so I`m asking for some assistance.How does a breaker lets say 40 amp double pole square D home line work to protect agaist fault current.

Top
2014 / 2011 NEC & Related Books and Study Guides
#86588 - 11/13/03 05:58 AM Re: breaker trip
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Most convebtional CB's have a thermal component which responds, (relatively slowly)
to lower level overloads in a manner which is inversely proportional (time v. current)to the overload.
There is also a magnetic component, which in the event of a ground-fault or short-circuit, will respond almost instantaneously to this, normally much higher level of overcurrent.

Top
#86589 - 11/13/03 08:01 AM Re: breaker trip
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Another term for how breakers and fuses react to overcurrent is an inverse time-current characteristic. Simply—the higher the current, the faster the device operates.

Detail: www.usace.army.mil/publications/armytm/tm5-811-14/

Quickie: www.cbibreakers.com/magnetic.asp?menu=sixth

Top