The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by sparky
58 minutes 49 seconds ago
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 261 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86048 - 09/03/03 07:59 AM Circuit Breakers
boxford Offline

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
What article in the NEC states that you can only utilize a circuit breaker up to 80% of its capacity?

2014 / 2011 NEC & Related Books and Study Guides
#86049 - 09/03/03 08:33 AM Re: Circuit Breakers
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
210.19(A)(1) & 215.3 provide limits for overcurrent protection of continuous loads

#86050 - 09/04/03 06:41 AM Re: Circuit Breakers
dana1028 Offline

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
(1999) 384-16(d) - Continuous Load
'The total load on any overcurrent device located in a panelboard shall not exceed 80% of its rating where, in normal operation, the load will continue for 3 hrs. or more.'

(2002) - In 2002 this section was deleted.[Proposal 9-107, ROP] It was contended that rules in 210.19(A), 210.20(A), and 215.3 cover this issue and this wording was unnecessary.

#86051 - 09/04/03 09:46 AM Re: Circuit Breakers
boxford Offline

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
Thank you very much I really appreciate it.

#86052 - 09/12/03 05:35 AM Re: Circuit Breakers
jnsells Offline
Junior Member

Registered: 08/26/03
Posts: 2
Loc: Nashville, TN
Most small molded-case breakers are only rated for 80% of their nominal rating. Larger frame molded case breakers can be specified as "100% rated" but will cost more. Best to check with the manufacturer.