The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86048 - 09/03/03 07:59 AM Circuit Breakers
boxford Offline
Member

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
What article in the NEC states that you can only utilize a circuit breaker up to 80% of its capacity?

Top
2014 / 2011 NEC & Related Books and Study Guides
#86049 - 09/03/03 08:33 AM Re: Circuit Breakers
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
210.19(A)(1) & 215.3 provide limits for overcurrent protection of continuous loads
_________________________
Ron

Top
#86050 - 09/04/03 06:41 AM Re: Circuit Breakers
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
(1999) 384-16(d) - Continuous Load
'The total load on any overcurrent device located in a panelboard shall not exceed 80% of its rating where, in normal operation, the load will continue for 3 hrs. or more.'

(2002) - In 2002 this section was deleted.[Proposal 9-107, ROP] It was contended that rules in 210.19(A), 210.20(A), and 215.3 cover this issue and this wording was unnecessary.

Top
#86051 - 09/04/03 09:46 AM Re: Circuit Breakers
boxford Offline
Member

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
Thank you very much I really appreciate it.

Top
#86052 - 09/12/03 05:35 AM Re: Circuit Breakers
jnsells Offline
Junior Member

Registered: 08/26/03
Posts: 2
Loc: Nashville, TN
Most small molded-case breakers are only rated for 80% of their nominal rating. Larger frame molded case breakers can be specified as "100% rated" but will cost more. Best to check with the manufacturer.