What article in the NEC states that you can only utilize a circuit breaker up to 80% of its capacity?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#86049 09/03/03 11:33 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
210.19(A)(1) & 215.3 provide limits for overcurrent protection of continuous loads


Ron
#86050 09/04/03 09:41 AM
Joined: Jan 2002
Posts: 163
D
Member
(1999) 384-16(d) - Continuous Load
'The total load on any overcurrent device located in a panelboard shall not exceed 80% of its rating where, in normal operation, the load will continue for 3 hrs. or more.'

(2002) - In 2002 this section was deleted.[Proposal 9-107, ROP] It was contended that rules in 210.19(A), 210.20(A), and 215.3 cover this issue and this wording was unnecessary.

#86051 09/04/03 12:46 PM
Joined: Mar 2003
Posts: 15
B
boxford Offline OP
Member
Thank you very much I really appreciate it.

#86052 09/12/03 08:35 AM
Joined: Aug 2003
Posts: 2
J
Junior Member
Most small molded-case breakers are only rated for 80% of their nominal rating. Larger frame molded case breakers can be specified as "100% rated" but will cost more. Best to check with the manufacturer.