The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85965 - 08/23/03 07:13 PM Burial depth 20A circuit
WiCeltic Offline
Member

Registered: 10/13/01
Posts: 20
Loc: Sheboygan, Wi. USA
Going from house to permanent pool, 20A circuit for pump, pump pulls 12A (more than 1/2 of circuit) so can't put convenience outlet on same circuit. Need to run another 20A circuit.(Not multiwire,2 hots, #12 grd & 2 neutrals) Was going to dig down 12" and run Sched 80 PVC, because having to run two 20A circuits, inspector says have to go down 18". Is that correct. It's not so much the extra digging, what's the big deal, one circuit or two?

Top
2014 / 2011 NEC & Related Books and Study Guides
#85966 - 08/23/03 07:46 PM Re: Burial depth 20A circuit
WebSparky Offline
Member

Registered: 02/21/03
Posts: 144
Loc: Cleveland, Ohio
300.5 states that PVC conduit is to have a cover of 18". Has nothing to do with # of circuits.
_________________________
Dave

Top
#85967 - 08/23/03 07:56 PM Re: Burial depth 20A circuit
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
If both of these circuits are GFCI protected I feel that Column 4 of Table 300-5 would permit the 12" burial depth. You would need to install GFCI breakers not just GFCI receptacles at the end of the circuit since the underground conductors need to be protected. I would also put both breakers on the same leg in the panel or the inspector could argue that you have more that 120 volts in the conduit even though they are separate circuits.

Curt
_________________________
Curt Swartz

Top
#85968 - 08/24/03 04:43 AM Re: Burial depth 20A circuit
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I have installed several in the manner that caselec described, especially coming off the same buss. All passed inspection.
Webspark, see note 4 to table 300.5 It should apply here.

Top
#85969 - 08/24/03 09:42 AM Re: Burial depth 20A circuit
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
If the wiring is within 5 feet of the pool 18" is required. Other than that the methods above look good to me.

Top
#85970 - 08/24/03 10:02 AM Re: Burial depth 20A circuit
WebSparky Offline
Member

Registered: 02/21/03
Posts: 144
Loc: Cleveland, Ohio
Redsy,

You are correct. I guess my lack of residential experience is showing! None the less, I should have read the notes!

Thanks!
_________________________
Dave

Top
#85971 - 08/24/03 02:11 PM Re: Burial depth 20A circuit
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I agree with 12" for the depth, as per 300.5 Expanding onto this...You are allowed the shallower burial depth because it is GFCI protected, correct? How do you guys fell about this: Does the entire circuit have to be GFCI protected (at the breaker), or does a GFCI receptacle outlet satisfy the requirement? Thanks in advance for your thoughts
_________________________
Ryan Jackson,
Salt Lake City

Top
#85972 - 08/24/03 06:37 PM Re: Burial depth 20A circuit
WiCeltic Offline
Member

Registered: 10/13/01
Posts: 20
Loc: Sheboygan, Wi. USA
Inspector here will let us come out of panel in basement, directly outside install 2 gang box with bubble cover, 1 GFCI recept 20A for convenience outlet, 1 GFCI "dead front" recept 20A feeding 20A 125V twist lock recept 5 feet from pool.
Thanks again Gentlemen for the replies, Don't often ask question, but do read the forums plenty, there is a ton of experience stated in the forums. I am a "old timer" but don't know it all. Just care about what I do, so really enjoy this group. Thanks

Top
#85973 - 08/24/03 07:14 PM Re: Burial depth 20A circuit
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
IrishMick

If you want to use the 12 inch burial depth, the entire circuit is to be GFCI protected. The concern of the burial depth is to protect a person if he/she should contact the cable with a shovel or the like. Protecting the pool pump with the GFCI breaker will 'kill two birds with one GFCI'

Pierre
_________________________
Pierre Belarge

Top
#85974 - 08/31/03 05:32 PM Re: Burial depth 20A circuit
LK Offline

Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
PVC 18" With GFCI We use rigid for pools 6" and a lot less digging. Only use PVC if the area in a swamp and always wet.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals