#85965 08/23/03 10:13 PM
Joined: Oct 2001
Posts: 20
W
Member
Going from house to permanent pool, 20A circuit for pump, pump pulls 12A (more than 1/2 of circuit) so can't put convenience outlet on same circuit. Need to run another 20A circuit.(Not multiwire,2 hots, #12 grd & 2 neutrals) Was going to dig down 12" and run Sched 80 PVC, because having to run two 20A circuits, inspector says have to go down 18". Is that correct. It's not so much the extra digging, what's the big deal, one circuit or two?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#85966 08/23/03 10:46 PM
Joined: Feb 2003
Posts: 138
W
Member
300.5 states that PVC conduit is to have a cover of 18". Has nothing to do with # of circuits.


Dave
#85967 08/23/03 10:56 PM
Joined: Apr 2002
Posts: 558
C
Member
If both of these circuits are GFCI protected I feel that Column 4 of Table 300-5 would permit the 12" burial depth. You would need to install GFCI breakers not just GFCI receptacles at the end of the circuit since the underground conductors need to be protected. I would also put both breakers on the same leg in the panel or the inspector could argue that you have more that 120 volts in the conduit even though they are separate circuits.

Curt


Curt Swartz
#85968 08/24/03 07:43 AM
Joined: Mar 2001
Posts: 2,056
R
Member
I have installed several in the manner that caselec described, especially coming off the same buss. All passed inspection.
Webspark, see note 4 to table 300.5 It should apply here.

#85969 08/24/03 12:42 PM
Joined: Jan 2002
Posts: 1,457
E
Member
If the wiring is within 5 feet of the pool 18" is required. Other than that the methods above look good to me.

#85970 08/24/03 01:02 PM
Joined: Feb 2003
Posts: 138
W
Member
Redsy,

You are correct. I guess my lack of residential experience is showing! None the less, I should have read the notes!

Thanks!


Dave
#85971 08/24/03 05:11 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
I agree with 12" for the depth, as per 300.5 Expanding onto this...You are allowed the shallower burial depth because it is GFCI protected, correct? How do you guys fell about this: Does the entire circuit have to be GFCI protected (at the breaker), or does a GFCI receptacle outlet satisfy the requirement? Thanks in advance for your thoughts


Ryan Jackson,
Salt Lake City
#85972 08/24/03 09:37 PM
Joined: Oct 2001
Posts: 20
W
Member
Inspector here will let us come out of panel in basement, directly outside install 2 gang box with bubble cover, 1 GFCI recept 20A for convenience outlet, 1 GFCI "dead front" recept 20A feeding 20A 125V twist lock recept 5 feet from pool.
Thanks again Gentlemen for the replies, Don't often ask question, but do read the forums plenty, there is a ton of experience stated in the forums. I am a "old timer" but don't know it all. Just care about what I do, so really enjoy this group. Thanks

#85973 08/24/03 10:14 PM
Joined: Jun 2003
Posts: 681
P
Member
IrishMick

If you want to use the 12 inch burial depth, the entire circuit is to be GFCI protected. The concern of the burial depth is to protect a person if he/she should contact the cable with a shovel or the like. Protecting the pool pump with the GFCI breaker will 'kill two birds with one GFCI'

Pierre


Pierre Belarge
#85974 08/31/03 08:32 PM
Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
PVC 18" With GFCI We use rigid for pools 6" and a lot less digging. Only use PVC if the area in a swamp and always wet.