#84829 - 05/09/03 06:00 AM Acceptable J-box?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Would a plastic nail-on device box, used as a junction box, with a blank (flush) plate be a violation of 110.3, if it is installed in an attic or unfinished basement?
Top
2017 / 2014 NEC & Related Books and Study Guides
#84830 - 05/09/03 11:51 AM Re: Acceptable J-box?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
If you comply with the box fill requirements, the box is NOT subject to physical damage, has no "unused" openings, and a proper cover, it is compliant with the NEC.
The above is MHO.
John
_________________________
John
Top
#84831 - 05/09/03 03:11 PM Re: Acceptable J-box?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Redsy, I agree with John. There is nothing prohibiting this installation. I kind of prefer plastic (non conductive) in some situations.

Roger
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals