Posted By: Redsy Acceptable J-box? - 05/09/03 01:00 PM
Would a plastic nail-on device box, used as a junction box, with a blank (flush) plate be a violation of 110.3, if it is installed in an attic or unfinished basement?
Posted By: HotLine1 Re: Acceptable J-box? - 05/09/03 06:51 PM
If you comply with the box fill requirements, the box is NOT subject to physical damage, has no "unused" openings, and a proper cover, it is compliant with the NEC.
The above is MHO.
John
Posted By: Roger Re: Acceptable J-box? - 05/09/03 10:11 PM
Redsy, I agree with John. There is nothing prohibiting this installation. I kind of prefer plastic (non conductive) in some situations.

Roger