#84074 - 03/06/03 12:20 PM a/c disconnect
khurst Offline
Junior Member
Registered: 03/06/03
Posts: 3
Loc: Hamilton,Ohio USA
The situation, there is a 1/0 seu ran to an outside raintight 8 circuit breaker box on a 125 amp breaker in the house.that is for disconnecting means for 3 air conditioners using 2-240 amp & 1-230 amp breakers leaving 2 available spaces. Is this a code violation?
Top
2017 / 2014 NEC & Related Books and Study Guides
#84075 - 03/06/03 03:25 PM Re: a/c disconnect
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
Hi khurst,

Ummmm... I'm not familiar with some of your terms..... which part of the description above are you concerned with?

Do you mean 2 two pole 40amp breakers?

seu?

Are you are asking about the acceptable means of disconnect? and/or amp size of breakers?

Dave
_________________________
Dave
Top
#84076 - 03/06/03 04:06 PM Re: a/c disconnect
khurst Offline
Junior Member
Registered: 03/06/03
Posts: 3
Loc: Hamilton,Ohio USA
Hi Dave,

Thanks for your reply
yes it would be 2 double pole 40 amp breakers 1 double pole 30 amp breaker my concern is the inspector says I can't have 2 available spaces left in this disconnect because there is no neutral in the disconnect
Thanks
khurst
Top
#84077 - 03/06/03 08:29 PM Re: a/c disconnect
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Khurst:
Welcome to ECN.....
Not trying to be a wise guy...what would the inspector say if you installed another 2 pole cb, and marked it "spare"?????

John
_________________________
John
Top
#84078 - 03/07/03 01:05 PM Re: a/c disconnect
khurst Offline
Junior Member
Registered: 03/06/03
Posts: 3
Loc: Hamilton,Ohio USA
I think I will try that, but what he is getting at is that the homeowner could come off that disconnect and add receptacles in the yard or some thing like that that requires a neutral


khurst
Top
#84079 - 03/07/03 01:24 PM Re: a/c disconnect
Creighton Offline
Member
Registered: 01/06/02
Posts: 59
Loc: Hayward, CA
This subject was discussed at length in a recent contractor-inspector meeting, and the result was that 110.3(B) requires a neutral to be run to the panelboard, even though it is not used. The manufacturer's instructions and drawing show a neutral termination, so a neutral must be run. Creighton
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals