The situation, there is a 1/0 seu ran to an outside raintight 8 circuit breaker box on a 125 amp breaker in the house.that is for disconnecting means for 3 air conditioners using 2-240 amp & 1-230 amp breakers leaving 2 available spaces. Is this a code violation?
|
|
|
|
Joined: Feb 2003
Posts: 138
Member
|
Hi khurst,
Ummmm... I'm not familiar with some of your terms..... which part of the description above are you concerned with?
Do you mean 2 two pole 40amp breakers?
seu?
Are you are asking about the acceptable means of disconnect? and/or amp size of breakers?
Dave
Dave
|
|
|
|
Joined: Mar 2003
Posts: 3
OP
Junior Member
|
Hi Dave,
Thanks for your reply yes it would be 2 double pole 40 amp breakers 1 double pole 30 amp breaker my concern is the inspector says I can't have 2 available spaces left in this disconnect because there is no neutral in the disconnect Thanks khurst
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Khurst: Welcome to ECN..... Not trying to be a wise guy...what would the inspector say if you installed another 2 pole cb, and marked it "spare"?????
John
John
|
|
|
|
Joined: Mar 2003
Posts: 3
OP
Junior Member
|
I think I will try that, but what he is getting at is that the homeowner could come off that disconnect and add receptacles in the yard or some thing like that that requires a neutral
khurst
|
|
|
|
Joined: Jan 2002
Posts: 59
Member
|
This subject was discussed at length in a recent contractor-inspector meeting, and the result was that 110.3(B) requires a neutral to be run to the panelboard, even though it is not used. The manufacturer's instructions and drawing show a neutral termination, so a neutral must be run. Creighton
|
|
|
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
|
|
|
|
|