The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 253 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82214 - 10/24/02 03:55 PM Seperate Service
chick Offline
Junior Member

Registered: 10/24/02
Posts: 3
Loc: louisville, kentucky
given a single family dwelling, and a detached garage that has a 12 circuit panel installed, that is protected with a 50A breaker being fed by a 3 wire lateral from a 50 A main at the main panelboard and that has a driven ground should this panel be considered a seperate service and have the neutral bonded to ground?

thank you for any responses.

2014 / 2011 NEC & Related Books and Study Guides
#82215 - 10/25/02 04:06 AM Re: Seperate Service
sparky Offline

Registered: 10/18/00
Posts: 5545
yes per 250.32

#82216 - 10/25/02 04:37 AM Re: Seperate Service
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
See 250.32(B)(2) regarding metallic paths. These could include non-electric utility lines.