The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 133 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82214 - 10/24/02 03:55 PM Seperate Service
chick Offline
Junior Member

Registered: 10/24/02
Posts: 3
Loc: louisville, kentucky
hi,
given a single family dwelling, and a detached garage that has a 12 circuit panel installed, that is protected with a 50A breaker being fed by a 3 wire lateral from a 50 A main at the main panelboard and that has a driven ground should this panel be considered a seperate service and have the neutral bonded to ground?

thank you for any responses.
chick

Top
2014 / 2011 NEC & Related Books and Study Guides
#82215 - 10/25/02 04:06 AM Re: Seperate Service
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
yes per 250.32

Top
#82216 - 10/25/02 04:37 AM Re: Seperate Service
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
See 250.32(B)(2) regarding metallic paths. These could include non-electric utility lines.