#82214 10/24/02 06:55 PM
Joined: Oct 2002
Posts: 3
C
chick Offline OP
Junior Member
hi,
given a single family dwelling, and a detached garage that has a 12 circuit panel installed, that is protected with a 50A breaker being fed by a 3 wire lateral from a 50 A main at the main panelboard and that has a driven ground should this panel be considered a seperate service and have the neutral bonded to ground?

thank you for any responses.
chick

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#82215 10/25/02 07:06 AM
Joined: Oct 2000
Posts: 5,392
S
Member
yes per 250.32

#82216 10/25/02 07:37 AM
Joined: Mar 2001
Posts: 2,056
R
Member
See 250.32(B)(2) regarding metallic paths. These could include non-electric utility lines.