#81565 - 08/29/02 10:25 AM Light Fixtures
Tommy Offline
Junior Member
Registered: 08/29/02
Posts: 2
Loc: Southeast Coast
Can you install MC cable from fixture to fixture using the fixture support wires as the support for the MC cable also (without using separate junction boxes)? This is a commercial job. The cable ranges from 6' to 12'. Several people (including some inspectors) have said that it can be done this way. The problem that I am running into is that the inspecting engineer on this particular job sites it as a NEC violation if done this way.

I have found several code articles (330.30, 330.30B, 348, 376.56, 386.56, and 410.31) that read that it can be done this way. I have yet to find one that states it cannot.

If someone knows the exact article section in the NEC that states that it CANNOT be done this way, please let me know.

Thanks,

Tommy

[This message has been edited by Tommy (edited 08-29-2002).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#81566 - 08/29/02 01:15 PM Re: Light Fixtures
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
That is an important subject. The 'inspecting engineer' may not hold the authority of an AHJ, but may have something more important—direct influence on whether you or your employer get paid in a timely manner.




[This message has been edited by Bjarney (edited 08-30-2002).]
Top
#81567 - 08/29/02 01:20 PM Re: Light Fixtures
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Tom,

If the job is spec'd out by an engineer and you don't follow the engineers spec's, then I think the AHJ can fail the job. You are suppose to install a job as per the manufactures instructions and as per the engineer/architect designs it. It is not always a NEC code violation.
Top
#81568 - 08/29/02 07:37 PM Re: Light Fixtures
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Tommy:
There is a thread in "General Discussions" that has the same question that you asked here.
Are you asking if the MC cable can be supported by the ceiling grid support wires?
OR
Are you asking about the length of the MC cable from fixture to fixture?

If the "Inspecting Engineer" says that it's a violation, then the NEC Article should be referenced by him.

Please read my comments in the other thread...

I'll post the NEC article tommorow. my book is in my truck & it's raining...
HotLine1
John
_________________________
John
Top
#81569 - 08/30/02 05:31 AM Re: Light Fixtures
Geno Offline
Member
Registered: 08/27/01
Posts: 16
Loc: Syracuse, NY USA
Check 330.30(B) and 300.11
Top
#81570 - 08/30/02 06:19 AM Re: Light Fixtures
Tommy Offline
Junior Member
Registered: 08/29/02
Posts: 2
Loc: Southeast Coast
Thanks for all of your responses.

Bjarney: You're absolutely correct!

HEndean: This job was drawn up by a different engineer other than the one who is now inspecting the final job. The original plans did not specifiy the use of boxes. The job was completely installed per manufactures instructions and designs.

John: My question is can you run MC cable from fixture to fixture if supported independant to the ceiling system? Again, the length averages between 6' and 12'. Per my interpretation of the code, I can. The inspector's interpretation of the code is that I cannot.

Geno: I have read those code sections.

Thanks again for all of your responses.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
01/23/17 12:27 AM
License exam
by TRUE POWER
01/22/17 11:33 PM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, sparkyinak), 82 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals