The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Today at 08:46 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 296 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#81517 - 08/24/02 10:10 AM 240.4(B) when?
triple Offline

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
I am uncertain as to when this section can be sited as a reason for utilizing a breaker with a rating above the ampacity of the conductors being protected. Say, for instance, the ampacity (after all derating) of a set of service conductors is 380A. Since, according to 240.6(A), standard breaker size jumps from 350 to 400A, can the conductors with an ampacity of 380A feed a 400A service?

2014 / 2011 NEC & Related Books and Study Guides
#81518 - 08/24/02 10:19 AM Re: 240.4(B) when?
caselec Offline

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
The 380 amp conductors may be protected by a 400 amp over current device but the maximum calculated load on these conductors can not exceed 380 amps.
Curt Swartz

#81519 - 08/29/02 08:24 AM Re: 240.4(B) when?
safari Offline

Registered: 11/06/01
Posts: 11
Loc: Newport, Oregon, USA
For service over current protection and conductor coordination you must look in services because the rules are diferent.


This does not allow for selection of the next higher size of over current protection.


#81520 - 08/29/02 01:32 PM Re: 240.4(B) when?
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Rounding up to the next standard size is permitted. Take a look at 230.90(A) exception 2 and if you have the handbook, see the commentary following the exception.