The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 03:29 PM
Looking for older post
by Texas_Ranger
Today at 03:22 PM
Safety at heights?
by gfretwell
Today at 02:19 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#81517 - 08/24/02 10:10 AM 240.4(B) when?
triple Offline
Member

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
I am uncertain as to when this section can be sited as a reason for utilizing a breaker with a rating above the ampacity of the conductors being protected. Say, for instance, the ampacity (after all derating) of a set of service conductors is 380A. Since, according to 240.6(A), standard breaker size jumps from 350 to 400A, can the conductors with an ampacity of 380A feed a 400A service?

Top
2017 / 2014 NEC & Related Books and Study Guides
#81518 - 08/24/02 10:19 AM Re: 240.4(B) when?
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
The 380 amp conductors may be protected by a 400 amp over current device but the maximum calculated load on these conductors can not exceed 380 amps.
_________________________
Curt Swartz

Top
#81519 - 08/29/02 08:24 AM Re: 240.4(B) when?
safari Offline
Member

Registered: 11/06/01
Posts: 11
Loc: Newport, Oregon, USA
For service over current protection and conductor coordination you must look in services because the rules are diferent.

230.90.A

This does not allow for selection of the next higher size of over current protection.

tom

Top
#81520 - 08/29/02 01:32 PM Re: 240.4(B) when?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Rounding up to the next standard size is permitted. Take a look at 230.90(A) exception 2 and if you have the handbook, see the commentary following the exception.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top