#81517 08/24/02 01:10 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
I am uncertain as to when this section can be sited as a reason for utilizing a breaker with a rating above the ampacity of the conductors being protected. Say, for instance, the ampacity (after all derating) of a set of service conductors is 380A. Since, according to 240.6(A), standard breaker size jumps from 350 to 400A, can the conductors with an ampacity of 380A feed a 400A service?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#81518 08/24/02 01:19 PM
Joined: Apr 2002
Posts: 558
C
Member
The 380 amp conductors may be protected by a 400 amp over current device but the maximum calculated load on these conductors can not exceed 380 amps.


Curt Swartz
#81519 08/29/02 11:24 AM
Joined: Nov 2001
Posts: 11
S
Member
For service over current protection and conductor coordination you must look in services because the rules are diferent.

230.90.A

This does not allow for selection of the next higher size of over current protection.

tom

#81520 08/29/02 04:32 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Rounding up to the next standard size is permitted. Take a look at 230.90(A) exception 2 and if you have the handbook, see the commentary following the exception.

Tom


Few things are harder to put up with than the annoyance of a good example.