#76980 - 04/09/01 09:07 AM NM B wires in between stud and insulation
arthur Offline
Junior Member
Registered: 03/26/01
Posts: 3
Loc: maple grove, mn, USA
Hi all,

I have to install outlets in the basement, the studs are 1.5" thick and the insulation is 1.5", the drywall is .5" ,this gives me at least 2" clearance from the concrete wall. If I put the NM B wires in between stud and insulation will this be up to CODE ? I'm thinking that that any 1.25" screw or nail can't reach the wire so this will be OK. I just don't want to remove the insulation and use conduit (?).

Thanks,

Arthur
Top
2017 / 2014 NEC & Related Books and Study Guides
#76981 - 04/09/01 01:28 PM Re: NM B wires in between stud and insulation
Mike Offline
Member
Registered: 02/21/01
Posts: 62
You can notch the front side of the studs and lay the romex in there and install metal nail plates over the romex. Keep the romex no less than 1 1/4" from the front of the studs for the vertical run(s) of romex to the outlet boxes (running parallel to the studs).
Top
#76982 - 04/09/01 01:39 PM Re: NM B wires in between stud and insulation
Mike Offline
Member
Registered: 02/21/01
Posts: 62
Correction; steel nail plate a minimum of 1/16" thick.
Top
#76983 - 04/09/01 08:30 PM Re: NM B wires in between stud and insulation
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Arthur,

I'm having a hard time picturing what you are talking about. Are these studs 'on the Flat' against the concrete wall? What type of insulation? I'm trying to figure out what you mean by going between the stud and insulation.

Quote:
the studs are 1.5" thick and the insulation is 1.5", the drywall is .5" ,this gives me at least 2" clearance from the concrete wall. If I put the NM B wires in between stud and insulation will this be up to CODE ?


Bill
Top
#76984 - 04/10/01 06:23 AM Re: NM B wires in between stud and insulation
arthur Offline
Junior Member
Registered: 03/26/01
Posts: 3
Loc: maple grove, mn, USA
The studs and the rigid insulation were already in placed by the builder. Shall I say 'can I put the wires in the gap between the stud and insulation' ? or simply at the side of the stud adjacent to the insulation ?

Thanks,

Arthur

Quote:
Originally posted by Bill Addiss:
Arthur,

I'm having a hard time picturing what you are talking about. Are these studs 'on the Flat' against the concrete wall? What type of insulation? I'm trying to figure out what you mean by going between the stud and insulation.

Bill
Top
#76985 - 04/10/01 07:58 PM Re: NM B wires in between stud and insulation
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Arthur,

You should be Ok if you can figure some way of securing the cable back there (all the way).

Make sure that you are using boxes of the proper cu. in. capacity.

Bill
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals