#5731 - 12/03/01 07:00 PM No juice in outdoor GFCI installation
petekarn Offline
Junior Member
Registered: 12/03/01
Posts: 2
Loc: Driftwood, TX
I recently installed an underground conduit (110VAC)underground and tested fine on the GFCI. After a week, there was no juice and GFCI failed test. Outlets I tapped into from the side of the house are also dead. Nothing tripped. DVM shows nothing across hot to neutral, but about .3VAC across hot to ground. This outlet is at the end of a loop. Any help is appreciated.
Top
Work Gear for Electricians and the Trades
#5732 - 12/03/01 07:40 PM Re: No juice in outdoor GFCI installation
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
Pete,

If the outlet that supplies the new GFI is dead you would need to check the fuse or breaker for that circuit.

Is there a switch to control these receptacles that is off?
Top
#5733 - 12/03/01 08:35 PM Re: No juice in outdoor GFCI installation
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Pete,

Welcome!
If I understand it correctly you connected to an existing outside outlet? If so, is there a GFCI that protected that outside outlet? It might be in the Bathroom, Basement, Garage etc. If you're not sure I'd look around for a tripped GFCI in one of those locations. Or, it could be a loose connection somewhere.

Bill
Top
#5734 - 12/04/01 06:57 AM Re: No juice in outdoor GFCI installation
Dallas Offline
Member
Registered: 08/07/01
Posts: 151
Loc: North Salem, IN 46165
My bet would be a loose or broken connection somewhere upstream of the added work. The new work was the "straw that broke the camel's back" to an existing weak connection.

Dallas
Top
#5735 - 12/04/01 06:26 PM Re: No juice in outdoor GFCI installation
petekarn Offline
Junior Member
Registered: 12/03/01
Posts: 2
Loc: Driftwood, TX
Well guys, looks like Bill had the answer. There was a GFCI stashed in a tight spot behind two AC cooling units. Reset it and life became much better. Just another case of my not eliminating the obvious first, no matter how hard it may be to believe! Thanks for all your posts.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals