#47257 - 01/12/05 06:47 PM Raintite EMT fittings
livetoride Offline
Member
Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
When installing the new Raintite connectors in a threaded device do you use the rubber washer? On some lights and boxes the female threads start resessed and you can't get but one or two threads but if you remove the washer you can get a good connection. I was taught if it was threaded it was water tight. What are your thoughts? Rod
Top
Work Gear for Electricians and the Trades
#47258 - 01/13/05 08:32 AM Re: Raintite EMT fittings
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
I haven't used them yet but I would say that you need the "O" ring. Threaded is not necessarily leak proof and this is especially the case with Bell boxes and connectors. It all depends on whether the full taper of the threads on the fitting or conduit fully engage the threads of the box. That's possible with threaded rigid or IMC conduit but with most fittings the limit is reached when the hex or shoulder contacts the box.

-Hal
_________________________
www.myphonetechs.com
Top
#47259 - 01/13/05 05:43 PM Re: Raintite EMT fittings
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Welcome to the forums!

THe fitting must be used as per the mfg instructions. There are/were an instruction/installation sheet in the last few boxes of RT EMT fittings we bought. I can't say fore sure, but I believe the O-ring is to be used. The UL listing of RT fittings was revoked a while back, as the 'old style' fittings were not 'RT'.

A gut answer will be "use the O-ring"

John
_________________________
John
Top
#47260 - 01/13/05 06:32 PM Re: Raintite EMT fittings
livetoride Offline
Member
Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
Danm not what I want to hear but I do see your point. On a horizontal run I am more worried about a tight connection, the threads are short I do not see how water can enter if you have 5 threads but what do I know I have only been at it for 26 yrs. Do we have to put rubber gaskets on ridgid too? I am not talking about the ring on the Emt just the crush washer. If 5 threads is good for explosion proof why is it not good for weather tite?
Top
#47261 - 01/13/05 06:59 PM Re: Raintite EMT fittings
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
Quote:
If 5 threads is good for explosion proof why is it not good for weather tite?


Because for explosion proof, all the threads do is provide a long enough path to cool the escaping gases below the ignition point of the surrounding atmosphere. They DO NOT have to completely prevent leakage.

Pipe threads generally aren't leakproof without some kind of sealant. Plumbers need to use teflon tape, pipe dope, etc. to keep threaded pipe joints from leaking.

I would use the O-ring unless the instructions say to omit it.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals