#47209 - 01/11/05 06:39 PM Sump pump outside
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
I have a customer that is moving his sump pump outside. It currently is in a crawlspace under his master bedroom, and he is tired of hearing it cycle on & off at night, so they are digging a hole just outside, running the drain tiles to it, and then piping it to the storm sewer.

I want to avoid GFI to avoid nusiance tripping flooding the lower level. Any suggestions? I'm thinking an in-use cover with a single receptacle wouldn't fly because that exception only applies to the garage and basement.

Any suggestions?


Can I clip the cord and run it into an AC disconnect?
Top
Work Gear for Electricians and the Trades
#47210 - 01/12/05 06:57 AM Re: Sump pump outside
Radar Offline
Member
Registered: 04/30/04
Posts: 349
Loc: Los Angeles, CA
Can't you find an applicable exception to the GFI requirement based on: a) receptacle location not readily accessable, or: b) single receptacle (not duplex) dedicated to equipment fixed in place (Art 210-8)?
_________________________
There are 10 types of people. Those who know binary, and those who don't.
Top
#47211 - 01/12/05 08:23 AM Re: Sump pump outside
kd Offline
Member
Registered: 12/14/04
Posts: 52
Hey, install a GFCI; it is required to protect people from shock. Perhaps install it on a wall indoors so it will not get moisture in it and feed the sump pump downstream. If it trips, try to find a 15 mili-amp tripping model. If that trips, you will have to replace the GFCI with a switch. At least you tried. I am assuming that it is a new sump pump or they cannot afford to get a new one.
Top
#47212 - 01/12/05 09:54 AM Re: Sump pump outside
Dave55 Offline
Member
Registered: 05/08/04
Posts: 697
Loc: Crystal Lake, Illinois, USA
I'd keep the power cord and install a single receptacle with a WWIU cover. GFCI protection isn't required or recommended.

Dave
Top
#47213 - 01/12/05 10:14 AM Re: Sump pump outside
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
There is no code exception for this appication. The only excecption to 210.8(A)(3) is for snow melting equipment. You have 3 choices, 1) install the GFCI, 2) install a hardwired pump, or 3) install a 240 volt cord connected pump.
Don
_________________________
Don(resqcapt19)
Top
#47214 - 01/12/05 05:36 PM Re: Sump pump outside
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
Thanks guys.

Don, I was thinking along the same lines as you, except I didn't think of your option 3.

I'll put this question to my AHJ, but do any of you see a problem with cutting off the end of the cord? I guess besides maybe that a plumber will be fiddling around with it when it comes time to replace it.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals