#46623 - 12/28/04 10:01 AM 600 amp panel feeders
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
I am looking at 600-amp 120/208 3-phase panel fed with 2 sets of parallel 300 kcmil. The lugs they terminate to are 75C.

Table 310-16 ('99, please excuse the archaic reference)
| 75 C | 90 C |

300 kcmil | 285 amps | 320 amps|
350 kcmil | 310 amps | 350 amps|

Am I right to say that this panel should be fed from 350's because of the temp rating on the lugs?

So if my above suspicions are correct, can I fix it like this:
There is a J-box relatively close to the panel. Can I just remove the 300's back to the J-box and split bolt 350's from the panel to the j-box? I guess that is assuming the lugs on the other side are 90C rated, which come to think about is unlikely.
Top
Work Gear for Electricians and the Trades
#46624 - 12/28/04 10:58 AM Re: 600 amp panel feeders
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
You may be alright the way it is depending on the load. If the calculated load is less than 570 amperes, I do not see a problem with using 240.4(B). By the way, you will not be able to use the 90°C rating of the conductor except for the purpose of derating. I do not believe there is any way you will be able to terminate at anything other than 75°C at that ampacity.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#46625 - 12/29/04 08:36 AM Re: 600 amp panel feeders
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Just to pick nits.

The temperature rating of the lugs, themselves, is not important. It is the temperature rating of the terminations that is important. The termination includes the lug, the device, and the enclosure. All of these factors are important.

I once had a contractor argue that because the lug supplied in a Square D fusible switch was rated AL90CU he could use the 90C column. But he was wrong. There is no UL Listed (or any other NRTL that I know of) overcurrent protective device with a termination temperature rating in excess of 75C.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (ampherder, sparkyinak), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals