You may be alright the way it is depending on the load. If the calculated load is less than 570 amperes, I do not see a problem with using 240.4(B). By the way, you will not be able to use the 90°C rating of the conductor except for the purpose of derating. I do not believe there is any way you will be able to terminate at anything other than 75°C at that ampacity.
Charlie Eldridge, Indianapolis,
Utility Power Guy